    Grounding. I need to pick your brains.

    Been running over ideas about grounding in my shack. Question about safety ground i.e. grounding my equipment.

    Been researching a bit and I'm getting confusing answers. I want to ground my equipment.

    I have a HF rig, Antenna tuner and a power supply. Each has a tie in for a ground strap.

    I plan on setting up like this: Each peice of equipment will have individual short braided copper lead to a copper bus bar. Copper bus bar will have one short 5-6 ft x 3 inch copper strap going to 8ft ground outside the shack. All short lead stuff.

    I get confused after this.

    Should I run more then 1 ground rod into the ground spaced so far apart maxing out at 3 ground rods?

    and THIS IS THE REALLY CONFUSING ONE:

    SHould this ground system run to the house grounding where the AC line comes into the house?

    I have been researching this on the net and I get conflicting answers... I had always been taught that one should never tie into the house or service ground... i think this is probably incorrect but im not sure. Some people say that tie into the house service ground, you risk setting up a ground loop and energizing your equipment which is bad. Others say isolating the equipment from the service main does the same thing and creates lightning hazard.

    If I should tie into the service ground, do I need to direct tie my ground rods to the service ground rod with copper wire or can attaching a cold water line to my ground rods do this for me?

    Which way should I do this?

    I am away from the house and dont have any access to my ARRL books and the ARRL has all thier important info parked behind the pay wall....err i mean members only area

    Thanks

    Brian
    Last edited by W5BRM; 09-15-2013 at 04:30 PM.
    .

  2. #2
    Orca Whisperer PA5COR's Avatar
    Join Date
    Feb 2009
    Location
    The Netherlands
    Posts
    12,188
    I have the same setup on the ground level here, 3 10 feet long copper pipes in the ground each 10 feet from eachother in triangle formation each cadwelded with very thick wire to eachother and the ground from the house ground, mandatory here to cconnect all grounds to eachother.

    That way the ground from the electricity service and your safety ground won't see a different potential when the lightning strikes.
    The connecting massive copperline is 1/4 inch and cadwelded to the groundrods and the service ground.
    And to the 3000 feet of copperwire in/on the ground serving as ground plane for the inverted L, which each are grounded on the end with a 8 feet copperpipe as well.
    The last bit was not needed, but i had enough of the pipe to be used for it anyway.
    Check your local code how to setup the ground to the service ground.
    "If the Republicans will stop telling lies about the Democrats, we will stop
    telling the truth about them." - Adlai Stevenson (1900-1965)
    “I’m not liberal/conservative, I’m anti-idiotarian.”
    At some point in the last 20 years, the left moved to the center, and the right moved into a mental institution

  3. #3
    Whacker Knot WØTKX's Avatar
    Join Date
    Aug 2008
    Location
    Lakewood, CO
    Posts
    26,758
    One of the best resources on the net for this topic.

    http://www.w8ji.com/ground_systems.htm
    "Where would we be without the agitators of the world to attach the electrodes
    of knowledge to the nipples of ignorance?" ~ Professor "Dick" Soloman



  4. #4
    Master Navigator W5BRM's Avatar
    Join Date
    Jan 2007
    Location
    Somewhere in Murica!
    Posts
    1,422
    Quote Originally Posted by PA5COR View Post
    I have the same setup on the ground level here, 3 10 feet long copper pipes in the ground each 10 feet from eachother in triangle formation each cadwelded with very thick wire to eachother and the ground from the house ground, mandatory here to cconnect all grounds to eachother.

    That way the ground from the electricity service and your safety ground won't see a different potential when the lightning strikes.
    The connecting massive copperline is 1/4 inch and cadwelded to the groundrods and the service ground.
    And to the 3000 feet of copperwire in/on the ground serving as ground plane for the inverted L, which each are grounded on the end with a 8 feet copperpipe as well.
    The last bit was not needed, but i had enough of the pipe to be used for it anyway.
    Check your local code how to setup the ground to the service ground.
    Ok so i should connect ground to the house service... Can this b done thru connecting to cold water pipes or do i need to run a line all the way from shack to the house service? Its a looong way. They are exactly opposite corner from each other and its about 100 ft via perimeter run vs 4 ft to an outside waterline spigot.

  5. #5
    La Rata Del Desierto K7SGJ's Avatar
    Join Date
    Feb 2010
    Location
    The Desert
    Posts
    16,791
    I've always subscribed to "any good grounding is better than none at all". If the cold water pipe is close, use it until you can improve on it. So long as it isn't PVC, that is. I would probably augment that with ground rods when possible. I'd follow Dave's advice and follow the link. It is the best site I've ever found on the topic.
    Last edited by K7SGJ; 09-15-2013 at 07:37 PM.
    A clear conscience is usually a sign of a bad memory

    RIP ALBI-W3MIV RIP RUSS-W5RB RIP BOB-VK3ZL





  6. #6
    Orca Whisperer
    Join Date
    Oct 2009
    Location
    Buffalo, NY
    Posts
    22,593
    To sum up: All ground is ground. All ground should be equal. If you have two separate ground, that are not bonded, you run the chances of having potential between them, and a "ground loop".

    So, all electrical safety grounds should be tied to the same thing, or bonded together.

    Now, that being said, why are you grounding your equipment?
    Big Giant Meteor 2020 - We need to make Earth Great Again

    http://www.coreyreichle.com

  7. #7
    Conch Master KJ3N's Avatar
    Join Date
    Jul 2009
    Location
    A secret cave in northern Delaware.
    Posts
    9,113
    Quote Originally Posted by KC2UGV View Post
    To sum up: All ground is ground. All ground should be equal. If you have two separate ground, that are not bonded, you run the chances of having potential between them, and a "ground loop".
    As previously discussed here, there are (generally speaking) 3 types of "ground": 1) Electrical Safety, 2) RF, and 3) Lightning. Nothing says those are all the same thing.

    So, all electrical safety grounds should be tied to the same thing, or bonded together.
    True.

    Now, that being said, why are you grounding your equipment?
    Probably, "because the books say I should". I don't believe everything I read in books, and especially what I read on the Internet(s). ;)

    I've never bothered to run any additional grounding of any kind. In certain situations like 2nd floor shacks, they will often cause more problems than they solve. My rule of thumb is to add grounding only when there's an actual problem.

    My equipment is plugged into a 3-prong AC outlet, which is my Electrical Safety ground. My antennas are dipoles and loops (which are balanced antennas that require no RF ground), and a couple of verticals with their own radials, that serve as the RF ground for those antennas. As to lightning ground, in the 10 years I've been here, I can think of only 1 strike that came close. It struck a neighbor's tree, which is higher than any of my antennas. I also have a 1,000 foot FM broadcast tower less than 1/4 mile from me. If anything is going to get hit, it's going to be that structure.

    As always, YMMV.
    Last edited by KJ3N; 09-17-2013 at 04:04 AM.
    "People Who Don't Want Their Beliefs Laughed at Shouldn't Have Such Funny Beliefs" -AD5MB

    "If someone tells you he believes in and talks to an invisible bunny named Harvey, you put him on medication and a regimen of therapy. If someone tells you he believes in and talks to God, well, that's perfectly acceptable. Why that's the case is impossible for me to fathom." - WP2XX



    Latest ClubLog entries.

  8. #8
    Orca Whisperer
    Join Date
    Oct 2009
    Location
    Buffalo, NY
    Posts
    22,593
    Quote Originally Posted by KJ3N View Post
    As previously discussed here, there are (generally speaking) 3 types of "ground": 1) Electrical Safety, 2) RF, and 3) Lightning. Nothing says those are all the same thing.
    Agreed, however, it appears he was asking about electrical grounding, which is what I meant that all grounds are the same, and should be.

    ...Probably, "because the books say I should". I don't believe everything I read in books, and especially what I read on the Internet(s). ;)

    I've never bothered to run any additional grounding of any kind. In certain situations like 2nd floor shacks, they will often cause more problems than they solve. My rule of thumb is to add grounding only when there's an actual problem.

    My equipment is plugged into a 3-prong AC outlet, which is my Electrical Safety ground. My antennas are dipoles and loops (which are balanced antennas that require no RF ground), and a couple of verticals with there own radials, that serve as the RF ground for those antennas. As to lightning ground, in the 10 years I've been here, I can think of only 1 strike that came close. It struck a neighbor's tree, which is higher than any of my antennas. I also have a 1,000 foot FM broadcast tower less than 1/4 mile from me. If anything is going to get hit, it's going to be that structure.

    As always, YMMV.
    Which is why I'm asking. Oft times, just grounding electrically to your third prong is sufficient. I ground all the equipment to the power supply chassis, which has a third prong, and I go not recall any issues that could be attributed to grounding issues.
    Big Giant Meteor 2020 - We need to make Earth Great Again

    http://www.coreyreichle.com

  9. #9
    Orca Whisperer PA5COR's Avatar
    Join Date
    Feb 2009
    Location
    The Netherlands
    Posts
    12,188
    Not true that living next to a high structure saves you from getting hit.
    My parents ( deceased) lived near a 14 story apartent building topped up with a metallc structure holding lots of antenna's on top of it all bonded liberally with thich ground wires running down the apartment building to ground.
    10 meters from that 180 feet high structure was a cental antenna box 3 fet high.
    Containing amplifirs annd stuff.
    That one got hit not the 180 feet higher apartment building 30 feet away from the box....
    Don't assume that you will be safe if a high structure nis next to you, always assume the worst case scenario.
    I do, and i have the ground here for the inverted L and the safety ground for lightning strikes.
    Several antenna's are 30 -40 feet higher as the house here, i don't take risks.
    Read the supplied link, it is a good one.
    "If the Republicans will stop telling lies about the Democrats, we will stop
    telling the truth about them." - Adlai Stevenson (1900-1965)
    “I’m not liberal/conservative, I’m anti-idiotarian.”
    At some point in the last 20 years, the left moved to the center, and the right moved into a mental institution

  10. #10
    Master Navigator W5BRM's Avatar
    Join Date
    Jan 2007
    Location
    Somewhere in Murica!
    Posts
    1,422
    ok thanks for the replies guys. Main issue is that I think I am going to have to rework my electrical receptacle outlets. About half the house outlets don't have the 3 prong plug. The place where I am planning on installing the shack has no 3 prongers. I have looked inside them before and I see 3 wires inside the box so I am fairly certain the house is reasonably up to code. We have a breaker panel instead of fuses anyway. Thats the primary reason why I have been so concerned about grounding my equipment. With the 2 prong receptacles I have now, I don't think I would get the safety ground at the equipment level. I know I could probably run a small strap to the plug screw in the center of the receptacle but I'm a little leary of that. I have been reading a lot of the link provided and I think I have a better understanding now of how it works and what I should do. Once I get the receptacles updated, I should be good to go. Wont bother setting up an outside ground unless I get RF inside the shack. I hope I wont as I have no plans on running an amp and my HF rig is only 100w. I can stop most of the RF with a simple turns of coax at the entrance.